| Most of what I am saying has to do with the US, I have no idea what happens in other countries. From what I can tell, this is the background information that is true about aluminum use in the US.
- In the 1960s they started using 1350 alloy aluminum wire, had problems with creep/cold flow, oxidation, strength, and thermal expansion - 1350 would oxidize to make high resistance connections, thermally expand and creep to make low surface area connections, and was a weak material to work with - Revised CO/ALR devices with indium plated terminals can usually be used with 1350 because the indium metal seals tightly to prevent corrosion, but doesn't solve the other problems (expansion, creep, strength). - After that fiasco, 8000-series aluminum alloys were used for aluminum wire. Stronger, less creep, less oxidation. With anti-oxidant compounds this works A-OK, problem pretty much solved. - Aluminum terminal blocks and bus bars use 6101 or 6061 (most of the time, for the ones that weren't recalled), more structurally optimized, not as oxidation resistant but often tin plated.
So we solved aluminum wire, but it never really returned to low-amerage branch circuit wiring in houses. Smallest aluminum you typically see is 4AWG for 50A circuits, but even there 6AWG copper is still used a lot. These installations of aluminum cable must use an anti-oxidant compound on all terminations, and they all much be rated for use with aluminum.
Now if you are gonna have to do that for every termination, using aluminum for branch circuit wiring would suck. But that isn't always true, as copper clad aluminum wire exists. You can get CCA wire in sizes as small as 12AWG for 15A circuits, and of course it is cheaper and lighter than the 14AWG copper counterpart.
This wire uses 8000-series aluminum alloy, and is coated in copper to prevent oxidation. No anti-oxidant needed. Almost all terminations rated for Cu are rated for Cu-clad Al. But the thermal expansion issue still persists, and some say the cold flow issue was not entirely eliminated with 8000-series alloys.
What do you think? Will aluminum catch on for residential again? Or is this another disaster?
|
|
|
|
Logged
|
"The only stupid question is the one left unasked" ~ Confucious (sort of) Public Lamp Spec Sheet
|
Laurens
Member
    
Offline
View
Posts
View Gallery
|
| If a house costs like €300.000 to 800.000 to build and buy the land for, i'm not gonna care about €500 in extra cost of cable. I'd rather have copper in my walls and just be able to terminate anything to everything using bog standard connectors.
Copper wire is expensive but not that expensive. I pay €1 per meter (give or take a few cents - less for larger rolls) for single core 2,5mm2 copper residential installation wire, rated for 16a 230v in the Netherlands and 20a 230v in Belgium. You write that stuff off in maybe 50 years or so if you install it right. The yearly cost is small compared to all the other things you gotta manage on a house.
|
|
|
|
Logged
|
|
Medved
Member
    
Online
Gender: 
View
Posts
View Gallery
|
| It is true, the aluminum is more than double the conductivity of copper per conductor weight (not cross section, really weight), also way cheaper, but these aspects are not that significant on thinner wires. There the surrounding accessory (the insulation, restriction to the cable assembly materials to prevent corrosion, more care so more expense needed for termination,...) either cost the same or even is more expensive with aluminum, so if the material/weight savings are not substantial, it does not make much sense.
Regardless of the exact composition, aluminum are all more prone to oxidation and creep problems. The improved composition made them less severe, but compare to copper, they are still there. And some of the ways how to address these problems means more expensive terminal designs. Now these problems affect mainly thinner conductors, the thicker the thing is, more resistant it becomes. So for relatively thin home installations they are way too much problem vs how much cost and weight savings it may offer vs copper, or the fixes for the aluminum problem become relatively expensive (big part of the extra termination cost to fix the aluminum problems does not depend on the size/rating of the connection, so for low current ones becomes pretty expensive). But for higher current, thicker conductors have inherently less problems to start with, plus the amount of material in question becomes so much it starts to make sense to invest into the more complex connection solutions.
And this is reflected in the standards - aluminum is allowed only 16mm^2 and above (AWG6 and thicker)
For normal home 16A circuit installation the 2.5mm^2 of copper is used (4mm^2 was used with Al), that in the equivalent 4mm^2 Al, was and in older installations still is causing permanent headaches with connection resistance faults.
Only the main feed and distribution lines, generally significantly thicker than the 16mm^2, are still installed and used with aluminum without any problems. But the important differentiator is the conductor size.
|
|
|
|
Logged
|
No more selfballasted c***
|
RRK
Member
    
Offline
Gender: 
View
Posts
View Gallery
Roman
|
| The problem with aluminum wiring was never 'solved' as it is physically/chemically fundamental. For smaller gauges there is also a significant corrosion problem. Of course, financial savings are large, and sometimes lower density of aluminum matters, so Al wiring is tolerated in professional installations. And thieves are not interested in stealing Al cables. Home wiring is more chaotic and less controlled by definition, and especially in US with 120V line voltage is unavoidably associated with huge currents. So, please NO )
|
|
|
« Last Edit: April 13, 2026, 02:07:11 AM by RRK »
|
Logged
|
|
rjluna2
Member
    
Offline
Gender: 
View
Posts
View Gallery

Robert
|
| Most remodelers I have seen at HGTV tells the viewer that the house with aluminium wiring should be replaced with copper wiring to bring it's up to code.
|
|
|
|
Logged
|
Pretty, please no more Chinese failure.
|
Medved
Member
    
Online
Gender: 
View
Posts
View Gallery
|
| Well, if it is up to code valid at build time, it is "up to code" now as well. Problem is, when the installation is too old, you will have troubles finding components compliant with code from that time. Especially things compatible with aluminum wires (switches, sockets, connection for pigtails,...).
|
|
|
|
Logged
|
No more selfballasted c***
|
Multisubject
Member
    
Offline
View
Posts
View Gallery

|
@Laurens That is true I suppose, wiring cost is relatively small @Medved I did not consider that those problems would be worse with smaller gauges that does make sense. Interesting how you have a minimum conductor size for aluminum use there.
|
|
|
|
Logged
|
"The only stupid question is the one left unasked" ~ Confucious (sort of) Public Lamp Spec Sheet
|
dor123
Member
    
Offline
Gender: 
View
Posts
View Gallery

Other loves are printers/scanners/copiers, A/Cs
|
It is true, the aluminum is more than double the conductivity of copper per conductor weight (not cross section, really weight), also way cheaper, but these aspects are not that significant on thinner wires. There the surrounding accessory (the insulation, restriction to the cable assembly materials to prevent corrosion, more care so more expense needed for termination,...) either cost the same or even is more expensive with aluminum, so if the material/weight savings are not substantial, it does not make much sense.
Regardless of the exact composition, aluminum are all more prone to oxidation and creep problems. The improved composition made them less severe, but compare to copper, they are still there. And some of the ways how to address these problems means more expensive terminal designs. Now these problems affect mainly thinner conductors, the thicker the thing is, more resistant it becomes. So for relatively thin home installations they are way too much problem vs how much cost and weight savings it may offer vs copper, or the fixes for the aluminum problem become relatively expensive (big part of the extra termination cost to fix the aluminum problems does not depend on the size/rating of the connection, so for low current ones becomes pretty expensive). But for higher current, thicker conductors have inherently less problems to start with, plus the amount of material in question becomes so much it starts to make sense to invest into the more complex connection solutions.
And this is reflected in the standards - aluminum is allowed only 16mm^2 and above (AWG6 and thicker)
For normal home 16A circuit installation the 2.5mm^2 of copper is used (4mm^2 was used with Al), that in the equivalent 4mm^2 Al, was and in older installations still is causing permanent headaches with connection resistance faults.
Only the main feed and distribution lines, generally significantly thicker than the 16mm^2, are still installed and used with aluminum without any problems. But the important differentiator is the conductor size.
If aluminum have more electrical conductivity than cooper, why most ballast wires are made from cooper and why most electrical cables are made from cooper?
|
|
|
|
Logged
|
I"m don't speak English well, and rely on online translating to write in this site. Please forgive me if my choice of my words looks like offensive, while that isn't my intention.
I only working with the international date format (dd.mm.yyyy).
I lives in Israel, which is a 220-240V, 50hz country.
|
Medved
Member
    
Online
Gender: 
View
Posts
View Gallery
|
| Al is better conductor per weight (measured as resistance of given length of wire with each of such thickness so both have the same weight; because Al has about 3.3x lower density, for the same mass it will be 3.3x thicker cross section, so even with about 1.6x higher specific resistivity it yields about 2x lower resistance of that wire), not dimension (cross section). Because with ballast what matters is the volume, not weight, because that dictates how heavy the core would be (larger volume for the winding means taller the ballast core legs, so more steel in them, so the total weight or cost saving won't offset the larger ballast size). But some ballasts were made using aluminum wire, mainly US HX and CWA's, the calculation probably made it seem worth. The main problem with AL for winding I would see the inherent fragility of the Al wire, moreover when that thin, resulting into reliability problems. And these problems then are not worth the savings, even if those were real.
|
|
|
|