I have a a striplight that I put up in my utility room that came with a no name electronic rapid start ballast that said it could run F32T8 or F40/34T12s. I'm currently running T8s in it right now butI wonder if the lectronic rapid start F32T8 ballast will run the F40 better than the IS ballasts since the cathodes should be heated like the F40 ballasts.
Only ghetto ballasts will endorse that. There are many ballasts that do not even meet ANSI specs.
On a 2-4' rated ballasts, an F40T12 will run at about 80% the power of F32T8 based on my measurements. Since the ballast is constant current and lamp determines the voltage, 25.6W would mean that to the ballast, it's just like driving a F25T8, or F32T8/25W.
Ballast spec includes supported lamps, and ballast factor rating.
A common T8 normal ballast has a BF of 0.87, which means that when a lamp is operated on that ballast, the lamp's output will be 87% of catalog spec.
A normal magnetic ballast usually is rated 0.95.
What these F40T12/F32T8 compatible ballasts don't tell you is the difference in ballast factor.
F40T12 will run at 80% of F32T8. Since the F32T8 is already driven at 87% of spec, this means that F40T12 can be estimated to produce rated 87% on T8 * 80% of T8 * 32W/40W = 56%
You can get T12s to run at close to 70% output if you use a 1.20 BF high-light ballast (not to be confused with "high output" which is designed for a different system).
If you use a Sylvania PSH high-light T8 ballast(which is rated for F17 to F32 and F40T12 is similar to F25T8 once running) with T12 lamps, you should get an acceptably good (70% of rated lamp spec) output and good life.