Addressing the article points :
Whats right :
Bad circuit breakers - Seen those. Its not much about their age, but some are simply made too bad - they were unreliable to the same extent when they were new. My friend had a breaker that did not trip once after a short circuit (tripped the main but not the branch). I did not like it. Plugged in a test lamp, flipped the breaker off, but it did not feel right (like the handle is doing nothing). lamp still on. Hit the side of the breaker with the screwdriver, then there was a click in it and the lamp went off
Bad RCD (GFCI's) - seen this too. But their claim for "limited life" of the breaker is debatable - Its pretty simple lectromechanic device, and as such supposed to last forever. In all 30+ year old RCD's from reputable manufacturers i seen, when i pressed Test they tripped. Some cheaper RCDs did not trip even though they are not that old. OTher thing, i seen such cheap RCD's fail with arcing switch (internal) contacts (and melted enclosure) which menas that they mighthave started a fire in their own right rather than protecting from a fire
(RCD's are meant for protection in case of electric shork and not for fire prevention, but in fact they do prevent some fires by tripping in
"stray curent" cases where the small leakage current can go through pretty dangerous path ie wet drywall etc)
Load on the system - well he is right. There are many issues, see below
Now what i call BS :
"The electric blanket" is listed along with heating appliances as a "heavy appliance" - Hey eletrician, go and look before you write. Most of them are less than 100W powre consumption. Yes, the blanket can be dangerous in its own ways but as a cause of overload

"The surge protector regulates the current going to the appliance" - Hey electrician, did you open one ? Its just 3 MOV's between L/N/E. It does not "regulate the current". If anything, it is only ANOTHER fire starter when you have open neutral - most surge protectors sold here are just MOV's no thermal protection, and they are rated at like 275-375V. Perfect for that bad neutral incidents
And what could be better :
"arcing sockets" - Basicaly he is right, but i vcan imagine that some folks will be eating video when they see that their laptop PSU is making a spark every time it is plugged in. Would be good idea to say that sparks are to be expected with stuff like this and it is normal. But look further. "Noises coming from power strips (transformers)". Hey electrician, power strips are NOT transformers
"power strips" - Basically he is right, but worth mentiomning that power strips rated to 16A usually begin smoking at about 10A. Thats rihgt, our standards institute is busy with efficiency ratings of lamps instead of sotring out the consequences of that "16A mistake" from the 80s
And if i would write it i'd address this :
Heating appliances : Keep clearance in front of them. dont put them to dry stuff except radiators and A/C. The IR heaters and the heat fans have magic powers like IR and hot air. Stuff subjected to those things gets WAY hotter than you might think, especially the IR. You might think it is ok to put some clothes at 1m from th heater (cmon, its 1m, far enough), next thing they are on fire. Also dont use them on carpet. They can be tipped face down and thats it
Sockets : They can be loose, especially old ones. If you insert hte plug and dont feel that it goes tightly into the contacts, it means that it cannot hold much load. Ok for a cell phone charger, bad for a lamp, unacceptable for bigger electronics and any big appliances
Splitters and cables : They can be bad, loose, too thin. Open hte plugs and sockets and inspect that every screw is tihgtened well, isolation is complete etc. Dont load anything above 10A. Dont load switched power strips above 8A. I know its written 16A on them but trust me on this one
Mess behind the computer : All too often i see a stack of splitters and adapters in htere, which is so big that it is mechanically unstable. Dont let it be. Replace all that splitters to one or more power strips. The ampacity is unchanged ut nw you can be sure that all plugs are tightly inserted in the sockets. And dont let htat corner be dirty
Wiring in old homes : It is usually done with 1.5mm^2 in branches, yet most breakers are 16A. Check out which rooms each branch covers (its usually like this in old flats : living room+1 bedroom, bathroom+other bedroom, washing machine, water heater, kitchen).Dont load any such GROUP at above 12A continuous for 1.5mm^2 wiring
Wiring in old homes : Often badly comnnected. Especially common with wire nuts - They were used here untill hte 70s (and few contractors used up the stock even in the 80s), yet looks like NOBODY knew how to use them properly, so its common to find several glowing connections in every flat wired with 1.5 and wire nuts. Go and find out
Upgrades : Often bathroom permanent devices like heaters and electric showers are wired to existing wiring. Now thats BAD. Electric shower takes over 20A which should go on 4mm^2 (not even 2.5), but i seen electricians who tap it from the 1.5 wiring that used to be for the water tank (whose idea it was to use 1.5 for hte tank in the 1st place

). I even seen some that tapped it from the light fixture!!!! (1.5 too) Anyway it can survive like that, mostly due to the fact that current is drawn briefly. But what, you open the ater for a bit longer and get a fire ?
Bypassing the main breaker : If you are in an old flat in Israel just try this : Flip off the main breaker, and try to switch on the shower, the water heater, the A/C. The older the flat is, the higher chance that one of them will work with the main breaker off. And here is why : The main breaker in old flats is usually 25A. The shower alone takes 20+A. Few lights around the home 1-2A. Electronics 2-3A. Room heater 10A. Together 33-35A. Now look at the trip curve for "C" breakers - That'd trip exactly few minutes into the shower, when you are all over in soap. The user complained to the electrician. Now the correct thing to do is to order service upgrade from the electric company, which is expensive. What cheap electrician does is move the shower to take its power from before the main - so that the shower is on is own breakre and thats it. Nevermind the hack is usually done with 2.5's..
Besides, electric shower powered from before the main means that there is no RCD protection to it. So if there is 240 in the shower head the RCD is nowhere to protect you
Medved :
Breakers not wswitching off - sen that actually happen to my friend
Dust in panel devices - seen it hasppen the other way - building debris gets into the contacts preventing them from closing well, and the switch is heating and arcing as it is used. But what yoiu say is possible too, esp. if the dust is really dust and not small concrete debris which is largely unflammable (which was the case in the incident i seen)
Loose screws - Common in copper too, since electricians dont tighten the screws in the first place (or worse, using wire nuts without hte slightest idea how to install them correctly), or use inappropriae wiring (using stranded wire without crimped ends to carry 25A to circuit breaker ? Really ?)
Xmas tree - I think it is supposed to let enough of a short current to trip the 16A breaker. But some chains use really scary thin wiring and bad connections, that may have just enough resistance to limit the current a bit.... And if it limit enough to prevent immediate tripping of the breaker then there can be fire