Author Topic: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains?  (Read 2377 times)
WorldwideHIDCollectorUSA
Member
*****
Offline

Gender: Male
View Posts
View Gallery

HID, LPS, and preheat fluorescents forever!!!!!!


Worldwide HIDCollectorUSA
Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « on: October 20, 2020, 04:41:00 PM » Author: WorldwideHIDCollectorUSA
I wonder if operating a Japanese 100v HID ballast designed for 50 or 60hz operation should cause any damage to the ballast if it is operated on a 120v 60hz supply?
Logged

Desire to collect various light bulbs (especially HID), control gear, and fixtures from around the world.

DISCLAIMER: THE EXPERIMENTS THAT I CONDUCT INVOLVING UNUSUAL LAMP/BALLAST COMBINATIONS SHOULD NOT BE ATTEMPTED UNLESS YOU HAVE THE PROPER KNOWLEDGE. I AM NOT RESPONSIBLE FOR ANY INJURIES.

Rommie
Administrator
Member
*****
Offline

Gender: Female
View Posts
View Gallery

Andromeda Ascendant


Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #1 on: October 20, 2020, 04:48:06 PM » Author: Rommie
120V is 20% above the rated input voltage, so I can't imagine the ballast would be thrilled about it, and the output voltage would be higher as well so the lamp might be overdriven somewhat. The tolerance isn't usually that high, but I'm not 100% certain. I would check with the ballast manufacturers to be sure.

Personally, I am not a fan of running any lamp or ballast in a circuit that it isn't designed for. That is to say if I have a 35W SOX lamp then I run it on a 35W SOX ballast. If I do not have or can't get a 35W SOX ballast, I wait until I can before I light the lamp. If I have a 40W fluorescent lamp ballast for example, I don't run a SOX lamp on it. If I have a 120V 60Hz ballast then I run it on a 120V 60Hz supply, not the 277V tapping on a 240V supply, even though I know  it will work.

But that's me, I have always been a perfectionist. One thing I hate is to see a lamp or ballast unnecessarily destroyed by improper use, especially if it's a rare item that cannot easily be replaced.


« Last Edit: October 20, 2020, 04:55:15 PM by sox35 » Logged

Ria (aka Rommie) in Aberdeen
Administrator, UK & European time zones. Any questions or problems, please feel free to get in touch :love:

"What greater gift than the love of a cat..?" - Charles Dickens
*** No smiley-only replies, please ***

joseph_125
Member
*****
Offline

Gender: Male
View Posts
View Gallery


GoL
Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #2 on: October 20, 2020, 05:01:03 PM » Author: joseph_125
I run 100v equipment using two ways. For low power items I have a small 120v to 100v buck transformer that I got from Japan. For higher power items, I just set my variac to 100v (verify with a voltmeter as the scale might be off) and run it like that.

I generally don't experiment with fiddling around with different gear types but there are some well accepted and tested substitutions on this site that I'll do.
Logged
Rommie
Administrator
Member
*****
Offline

Gender: Female
View Posts
View Gallery

Andromeda Ascendant


Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #3 on: October 20, 2020, 05:03:06 PM » Author: Rommie
I would be interested in a 120V to 100V transformer, it might come in useful. Where did you get it..?
Logged

Ria (aka Rommie) in Aberdeen
Administrator, UK & European time zones. Any questions or problems, please feel free to get in touch :love:

"What greater gift than the love of a cat..?" - Charles Dickens
*** No smiley-only replies, please ***

Ash
Member
*****
Offline

View Posts
View Gallery


Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #4 on: October 20, 2020, 05:26:44 PM » Author: Ash
For inductive loads, running 100V 50Hz gear on 120V 60Hz will actually get spot on current, as the V/Hz is the same. (This applies to lamps to limited extent, since lamp circuits are non linear - There  is the lamp arc voltage + and then the inductive impedances. But in many cases it compensates closely enough)

Alternatively, take an 120V to 12V/24V isolation transformer, rated for the current of your 100V load (so quite small VA actually), and wire it's secondary in series with the primary to create an autotransformer for your wanted voltage
Logged
joseph_125
Member
*****
Offline

Gender: Male
View Posts
View Gallery


GoL
Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #5 on: October 20, 2020, 05:44:54 PM » Author: joseph_125
I would be interested in a 120V to 100V transformer, it might come in useful. Where did you get it..?

I picked mine up at the airport in Tokyo but I found a few on eBay. I recall there also being a 240v to 100v transformer too.

I got it mostly to run a Japanese exit sign I picked up so the low power output was perfect for it.
« Last Edit: October 20, 2020, 05:51:56 PM by joseph_125 » Logged
Medved
Member
*****
Offline

Gender: Male
View Posts
View Gallery

Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #6 on: October 20, 2020, 06:49:50 PM » Author: Medved
The ballast maker will tel for sure. But very likely it is not fromally rated for anything else.
Then it depends what ballast we are talking about. If it is a series choke (it will probably have one connection for 50Hz, other for 60Hz, if really rated for both), then the "50Hz" connection will compensate for the 120V at 60Hz.
When it is electronic (so no reconnection/switching between 50/60Hz), the 120V may mean lamp overload.
If it is something like CWA (with capacitor), it would become quite difficult to convert to 120V.

So if rated 100V/60Hz, best would be to use an 120->100V autotransformer...
Logged

No more selfballasted c***

Bulbman256
Member
*****
Offline

Gender: Male
View Posts
View Gallery

Mad Max


Bulbman256
Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #7 on: October 20, 2020, 09:45:56 PM » Author: Bulbman256
If it was incadecent, then i say get a transformer. But if it was a cfl/led that could Handel eh voltage variation better then run it straight off of the grid.
Logged

Collecting light bulbs since 2012, a madman since birth.

WorldwideHIDCollectorUSA
Member
*****
Offline

Gender: Male
View Posts
View Gallery

HID, LPS, and preheat fluorescents forever!!!!!!


Worldwide HIDCollectorUSA
Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #8 on: June 22, 2023, 10:42:19 PM » Author: WorldwideHIDCollectorUSA
For inductive loads, running 100V 50Hz gear on 120V 60Hz will actually get spot on current, as the V/Hz is the same. (This applies to lamps to limited extent, since lamp circuits are non linear - There  is the lamp arc voltage + and then the inductive impedances. But in many cases it compensates closely enough)

Alternatively, take an 120V to 12V/24V isolation transformer, rated for the current of your 100V load (so quite small VA actually), and wire it's secondary in series with the primary to create an autotransformer for your wanted voltage

Should a 100v 50Hz HX autotransformer ballast be safe on a 120v 60Hz mains supply as well?
Logged

Desire to collect various light bulbs (especially HID), control gear, and fixtures from around the world.

DISCLAIMER: THE EXPERIMENTS THAT I CONDUCT INVOLVING UNUSUAL LAMP/BALLAST COMBINATIONS SHOULD NOT BE ATTEMPTED UNLESS YOU HAVE THE PROPER KNOWLEDGE. I AM NOT RESPONSIBLE FOR ANY INJURIES.

Medved
Member
*****
Offline

Gender: Male
View Posts
View Gallery

Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #9 on: June 23, 2023, 02:57:17 AM » Author: Medved
It may yield very similar current, but it should be carefuly verified by measurement.
What will differ is the OCV and so the slope how the current changes with the arc voltage variation, which will be OK for unsaturated lamps (e.g. MV), but may cause worse thermal stability for saturated vapor types (e.g. HPS).
Plus the 20% higher OCV will pose about 40% (or even more) higher power dissipation load on the resistor in the ignitor when the lamp won't ignite (lamp failure, hot restrike,...), which may be too much so may cause earlier ignitor failure. So would require better care to make sure the ballast is not exposed to open load when powered.
Logged

No more selfballasted c***

WorldwideHIDCollectorUSA
Member
*****
Offline

Gender: Male
View Posts
View Gallery

HID, LPS, and preheat fluorescents forever!!!!!!


Worldwide HIDCollectorUSA
Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #10 on: June 23, 2023, 03:12:58 AM » Author: WorldwideHIDCollectorUSA
If the ballast’s secondary voltage (OCV) is higher, can using an ignitor designed for a higher supply voltage help remedy such situations?
« Last Edit: June 23, 2023, 03:34:31 AM by WorldwideHIDCollectorUSA » Logged

Desire to collect various light bulbs (especially HID), control gear, and fixtures from around the world.

DISCLAIMER: THE EXPERIMENTS THAT I CONDUCT INVOLVING UNUSUAL LAMP/BALLAST COMBINATIONS SHOULD NOT BE ATTEMPTED UNLESS YOU HAVE THE PROPER KNOWLEDGE. I AM NOT RESPONSIBLE FOR ANY INJURIES.

Medved
Member
*****
Offline

Gender: Male
View Posts
View Gallery

Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #11 on: June 23, 2023, 05:03:33 AM » Author: Medved
Of course, it is exactly the real OCV of the ballast vs the OCV the ignitor is designed for...
Logged

No more selfballasted c***

Alex
Member
***
Offline

Gender: Male
View Posts
View Gallery

feel free to ask questions


Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #12 on: June 29, 2023, 08:16:41 AM » Author: Alex
I would be interested in a 120V to 100V transformer, it might come in useful. Where did you get it..?
Hello,


If I am correct you should be able to make yourself by running a 240V/48V transformer in a non isolating setup. If you put 120V in it you can get 99.6V out.

You connect primary and secondary in series. on one net you put neutral on the other the 120V. Between the connection were both coils are connected and neutral you should hav 17% less voltage than the input voltage. You just need to be carefull when putting it together that you make sure the coils are wound in the same direction

best regards,

Alex
Logged

Glück auf ⚒️

Rommie
Administrator
Member
*****
Offline

Gender: Female
View Posts
View Gallery

Andromeda Ascendant


Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #13 on: June 29, 2023, 08:17:28 AM » Author: Rommie
Worth a try, thanks.
Logged

Ria (aka Rommie) in Aberdeen
Administrator, UK & European time zones. Any questions or problems, please feel free to get in touch :love:

"What greater gift than the love of a cat..?" - Charles Dickens
*** No smiley-only replies, please ***

WorldwideHIDCollectorUSA
Member
*****
Offline

Gender: Male
View Posts
View Gallery

HID, LPS, and preheat fluorescents forever!!!!!!


Worldwide HIDCollectorUSA
Re: Is it dangerous to operate a Japanese 100v HID ballast on US 120v mains? « Reply #14 on: June 30, 2023, 01:35:31 AM » Author: WorldwideHIDCollectorUSA
If I am using 100v 50Hz magnetic preheat fluorescent series choke ballasts and 100v 50Hz magnetic preheat fluorescent HX autotransformer ballasts to run fluorescent lamps, should I be safe to run those ballasts on 120v 60Hz mains without the need of a step down transformer or a variac as long as the starter can tolerate the higher OCV?