is it possible to connect a 120v ballast to the load side of a Multi-Volt ballast to get 120/208/240/277 volts?
|
|
|
Logged
|
Collector of all things GE! Except for LEDs. Utility Company: SCE
|
WorldwideHIDCollectorUSA
Member
    
Offline
Gender: 
View
Posts
View Gallery

HID, LPS, and preheat fluorescents forever!!!!!!
|
Are you asking about using the ballast as a step up transformer to get access to 208v, 240v, and 277v mains supplies?
|
|
|
Logged
|
Desire to collect various light bulbs (especially HID), control gear, and fixtures from around the world.
DISCLAIMER: THE EXPERIMENTS THAT I CONDUCT INVOLVING UNUSUAL LAMP/BALLAST COMBINATIONS SHOULD NOT BE ATTEMPTED UNLESS YOU HAVE THE PROPER KNOWLEDGE. I AM NOT RESPONSIBLE FOR ANY INJURIES.
|
GE PM
Member
  
Offline
Gender: 
View
Posts
View Gallery

Ge Post Mount
|
|
|
Logged
|
Collector of all things GE! Except for LEDs. Utility Company: SCE
|
WorldwideHIDCollectorUSA
Member
    
Offline
Gender: 
View
Posts
View Gallery

HID, LPS, and preheat fluorescents forever!!!!!!
|
Yes, you can certainly use a multi volt HID ballast as a step up transformer since all autotransformer ballasts use an integral step up transformer to provide an adequate secondary voltage to keep the intended lamp running.
|
|
|
Logged
|
Desire to collect various light bulbs (especially HID), control gear, and fixtures from around the world.
DISCLAIMER: THE EXPERIMENTS THAT I CONDUCT INVOLVING UNUSUAL LAMP/BALLAST COMBINATIONS SHOULD NOT BE ATTEMPTED UNLESS YOU HAVE THE PROPER KNOWLEDGE. I AM NOT RESPONSIBLE FOR ANY INJURIES.
|
BT25
Member
    
Offline
Gender: 
View
Posts
View Gallery

Vintage HID Collector Since 1985...
|
Use a 1000W MH ballast...this will give you more VA wiggle room.
|
|
|