Over here, distribution transofrmers (from 22kV phase-phase to 230/400V) are 3 phase, Delta primary, Y secondary. If there are similar transformers used in your grid then here is what might have happened :
Initially there was a short, either between phases or from a phase to ground. (Probably not to the LV wiring, as that would cause extensive damage in all connected properties and possibly some house fires)
There was either a remaining metal contact short, or remaining conductors in close proximity to each other, which would arc again when voltage is applied
After few reclosing attempts either the shorting part burned off, or the arc happened to not strike again anymore. In this case the substation does not see a fault anymore, so it has no reason to shut down again. (
@Medved)
However, one of the phase wires continuing towards your transformer was open circuit, so you got 2 phases and 1 open ended wire, connected to the 3rd phase of all transformers in the remaining part of the branch. For simplicity let's assume there is just your transformer there. Assume the broken HV phase is HV3
The transformer can be imagined as 3 individual transformers wired as follows :
T1 : Primary HV1-HV2 : Secondary L1-N
T2 : Primary HV2-HV3 : Secondary L2-N
T3 : Primary HV3-HV1 : Secondary L3-N
T1 is getting correct input voltage, and puts out the correct voltage on L1 (120V or 230V)
The wire HV3 is broken upstream, so it is only connected to T2 and T3. So T2 and T3 are effectively connected in series between HV1 and HV2
If the load on T2 and T3 is identical, the voltage will divide equally, each will get 1/2 of the voltage it is supposed to get on the input, and put out 1/2 of the normal voltage on the output
In practice the load is probably not identical, and will fluctate - especially as some loads either cut out from the undervoltage condition, or draw excessive current (such as motors unable to start) which may burn them open circuit or trip overload protections or breakers. If say L2 is loaded more, it will pull down the voltage of L2, and rise the voltage of L3. The sum of the two will be around 120V or 230V
In the US many transformers are single phase and wired Y on the primary i think ?
In this case, the transformers will be :
T1 : Primary HV1-HV0 : Secondary L1-N
T2 : Primary HV2-HV0 : Secondary L2-N
T3 : Primary HV3-HV0 : Secondary L3-N
(And they dont have to be all located in the same place)
As long as this is the circuit, HV3 and L3 will have no power at all, so just outage and not brownout. However :
- Three phase loads - whether a 3 phase transformer as above, or 3 phase LV load connected in Delta to the output of 3 individual transformers, will backfeed into HV3, and this way provide power to other transformers that are connected to HV3
- In SWER systems, the highly assymetrical load of HV1 and HV2 going to HV0, may cause voltage drop in the ground between HV0 and Earth near the location where there is high load. Now consider two single phase transformers connected between HV3-HV0 : One right next to the location with the high load, and one far away, but both in the bad area of the network. There is a voltage difference between HV0 in one and HV0 in the other location. The two transformers are connected between those locations in series (through the open HV3 wire), so they do get some voltage, and will output a matching voltage on the secondary (probably very low voltages in this case)