Curious question... What would be the effects of a capacitive load on a power system?
If the capacitive impedance becomes dominant, two problems will arise:
- It may cause the voltage on a long wiring end to become higher than at the source side. It is called "Ferranti effect" and in fact it is a result of the wire inductance to form a step up transformer. Those familiar with power RF knows this well, it happens with long wiring on a mains frequency too. The problem is, the usual distribution management sets the voltage at the distribution transformer to the allowed maximum, assuming the voltage will go down behind the line. Butonce the line is loaded with a capacitance and without much real power load, the voltage may go up, exceeding the upper bound without the management system knowing that.
- Other problems are running induction motors. The thing is, once you want to disconnect a leg, where you have induction motors, as well as too much capacitance, the disconnected system becomes a hugeselfexcited induction generator without any voltage regulation. That means a lot of the mechanical energy in the motors rotating mass turns into a strong overvoltage, limited just by motor core saturation. And that means more than double peak voltage, with huge energy behind. Way more severe overvoltage than the ferranti effect, even without any need for long wiring or so.
Mainly the second one is the reason, why all phase lag PF compensation is designed to remain a bit on the inductive side, never turn capacitive (here I mean just system parameter tolerances like capacitor capacitamce close to the maximum tolerance, not malfunctions like extinguished lamp,...).