What HID can run on fluorescent ballasts? « on: November 28, 2026, 07:14:16 PM » Author: stillaintjeff24
Since HID ballasts are really expensive and heavy, as I put up more HID I wonder what can run on a fluorescent ballast? Fluorescent ballasts seem to still be made, and there are a lot of variations as well. Mainly I wonder what can HPS run on, as those seem to be the most resistant to accidental over ballasting or arc instability. Anyone know?
Logged
RRK
Member
*****
Online

Gender: Male
View Posts
View Gallery
Roman


Re: What HID can run on fluorescent ballasts? « Reply #1 on: Today at 12:28:34 AM » Author: RRK
A choke is a choke and a leak transformer works like a leak transformer whatever it is called a fluorescent or HID ballast. So any magnetic ballast can run a HID lamp too assuming OCV, impedance and lamp burning voltage are okay. Some thought must be given to fluorescent ballasts with 4-wire tube connection. Fluorescent chokes can be easily manipulated by parallel and series connection to get a right impedance. Multiple identical leak transformers usually can be run in parallel to multiply output current, too.

High pressure lamps all generally dislike working on high frequency sources like electronic ballasts. LPS (call it HID or not) is widely known to run okay on both magnetic and electronic fluorescent ballasts.

To run a generic HPS lamp you need to add an ignitor, retrofit HPS will start on itself. Some long tube/multiple series American fluorescent ballasts can probably generate enough OCV to ignite some easy to start HPS lamps by themselves, tough the following low burning lamp voltage may appear as an overload. High power factor types with a series capacitor in the secondary circuit may be still ok with this.

« Last Edit: Today at 12:34:53 AM by RRK » Logged
Laurens
Member
*****
Offline

View Posts
View Gallery

Re: What HID can run on fluorescent ballasts? « Reply #2 on: Today at 01:26:05 AM » Author: Laurens
A 70w HPS lamp can run on a 80w MV choke ballast, which in turn is equal to 2 40w fluorescent choke ballasts parallel IIRC, if we are talking about 230v mains stuff.

The HPS lamp will have a hard time igniting, i managed to get it to ignite semi-reliably in 5 to 10 tries with a standard fluorescent starter parallel to it, but i cannot imagine this is great for the lamp. You might want to figure out something different to ignite them, such as a floating (with respect to mains gnd) CCFL inverter, with a blocking capacitor that reliably blocks the 50Hz mains that is present on the lamp, but lets the 30kHz of the inverter high voltage itself through.

Alternatively, find a 70w HPS with internal starter explicitely meant for use on MV choke ballasts.

A SOX 18w (technically not HID, the discharge is 'soft' and not concentrated) will happily run on a 15-18w choke ballast with a fluorescent lamp starter in series with a capacitor like this: https://youtu.be/1DfxKqt4CLY
« Last Edit: Today at 01:29:30 AM by Laurens » Logged
RRK
Member
*****
Online

Gender: Male
View Posts
View Gallery
Roman


Re: What HID can run on fluorescent ballasts? « Reply #3 on: Today at 07:34:13 AM » Author: RRK
@stillaintjeff24 states he is in Florida, so it is 120V realm. In 120V world, leak transformer type fluorescent ballasts are more likely to encounter, though short tube ballasts like 1x15 and 1x20 or 1x8W are still expected to be simple chokes. It is perfectly possible to run a low voltage American HPS lamp, say 70W S62 one with a group of such chokes in parallel, adjusted to a proper impedance. A suitable ignitor is still needed, probably a starter with a lightbulb in series. I don't like the idea of a starter with a capacitor in series, as the resulted ignition is very harsh on lamp electrodes.