The pulse start lamps need HV pulses (in the order of few kV) to ignite the arc in the burners, so the ballast generate these until it senses the arc becoming present (well, it senses the voltage - arc present => below 150V, arc not yet present, above 200V with the pulse MH). This means all the equipment is designed to handle that high voltage, including the lamp internals.
The MV's are designed to have the arc ignited by the auxiliary probe on just the 230..300VAC ballast OCV, so their design is made to handle just that. That means the high voltage from the ignitor may be above what the structures in the outer are capable to handle, so actually ignite the arc there.
With these, the arc always ignites oon the place with the lowest breakdown voltage. With the first time turn ON, it was inside of the main arctube, so in fact it struck the arc where the arc is supposed to be, so everything worked well. When you have tried to restart the hot lamp, the hjigh pressure inside of the hot arc tube made the breakdown voltage there high, so the next place becomes somewhere between the support wires in the outer and the ballast struck the arc there. And because these structures are not designed to carry an arc, they have failed (the arc root heated them up, so the incandescence, till they have melted)...
The pulse start lamps are designed with their internal structures so, the breakdown would need way higher voltage than the few kV coming from the ballast, just because the attempt to hot start the lamp is a thing to expect during the normal life, but the MV is not supposed to be exposed to such high voltages.
So you have made a good practical experience to really not connect any probe start lamp on any pulse start ballast with the ignitor still connected.
And side note: The 250W ballast will severely overdrive the 175W lamp (if I remember well, 250W pulse start is rated for 3A, 175W MV for just 1.8A)
|