Re: 480 volts « Reply #15 on: September 16, 2017, 04:08:44 PM » Author: Ash
and you could use a 120 to 30 volt transformer and simply apply 120 to the 30 volt side
That you can't, the thing will saturate...
Logged
Keyless
Member
****
Offline

View Posts
View Gallery

Re: 480 volts « Reply #16 on: September 16, 2017, 10:02:02 PM » Author: Keyless
If this is permanent, I would just change the ballast. Technically speaking, lighting over 120 volts is not allowed in residential settings in the US. From the 2014 NEC:


Quote
210.6 Branch-Circuit Voltage Limitations. The nominal
voltage of branch circuits shall not exceed the values permitted
by 210.6(A) through (E).

(A) Occupancy Limitation. In dwelling units and guest
rooms or guest suites of hotels, motels, and similar occupancies,
the voltage shall not exceed 120 volts, nominal, between
conductors that supply the terminals of the following:

(1) Luminaires

(2) Cord-and-plug-connected loads 1440 volt-amperes,
nominal, or less or less than 1⁄4 hp
Logged
Lodge
Member
*****
Offline

View Posts
View Gallery

18W Goldeye / 52W R&C LED front door lighting


Re: 480 volts « Reply #17 on: September 16, 2017, 10:39:25 PM » Author: Lodge
If the control transformer is mounted in the fixture it meets code because your feeding it with 120, what happens in the fixture stays in the fixture, but you are right just change out the ballast, it's the safest, simplest and more the likely the cheapest..
Logged
xelareverse
Member
*****
Offline

View Posts
View Gallery

Re: 480 volts « Reply #18 on: September 17, 2017, 10:08:01 AM » Author: xelareverse
Be safe, get a new ballast
Logged

Save all the cool old stuff, and even the not so cool/old stuff. It'll be cool eventually. One day people will look back and feel nostalgia.

Keyless
Member
****
Offline

View Posts
View Gallery

Re: 480 volts « Reply #19 on: September 17, 2017, 10:17:06 AM » Author: Keyless
@Lodge: 100% correct. The NEC does not cover whats inside the fixture or appliance. But the amount of iron involved in boosting the voltage to 4x would perhaps be more than the ballast already inside there. Heat build up might be an issue as well, but there is no way to know until testing it.

Any pics of the fixture? Most fixtures will take retrofit ballast mounts well. With LEDs taking over, ballasts are starting to run cheap. Ebay might have a new in box ballast for less than $50. 
Logged
wattMaster
Member
*****
Offline

Gender: Male
View Posts
View Gallery


WWW
Re: 480 volts « Reply #20 on: September 17, 2017, 11:44:34 AM » Author: wattMaster
Any pics of the fixture? Most fixtures will take retrofit ballast mounts well.
The fixtures
Logged

SLS! (Stop LED Streetlights!)

Keyless
Member
****
Offline

View Posts
View Gallery

Re: 480 volts « Reply #21 on: September 17, 2017, 01:56:29 PM » Author: Keyless
Those will easily take retrofit ballasts.
Logged
Ash
Member
*****
Offline

View Posts
View Gallery


Re: 480 volts « Reply #22 on: September 19, 2017, 02:54:47 PM » Author: Ash
If this is permanent, I would just change the ballast. Technically speaking, lighting over 120 volts is not allowed in residential settings in the US. From the 2014 NEC

Add a USB charger in each so it counts as "USB charger with light" instead of "luminaire"
Logged
wattMaster
Member
*****
Offline

Gender: Male
View Posts
View Gallery


WWW
Re: 480 volts « Reply #23 on: September 19, 2017, 04:55:04 PM » Author: wattMaster
How about "outdoor heater"? ;D
Logged

SLS! (Stop LED Streetlights!)

WorldwideHIDCollectorUSA
Member
*****
Offline

Gender: Male
View Posts
View Gallery

HID, LPS, and preheat fluorescents forever!!!!!!


UChBXesrxSalDTp79uMtfDvA
Re: 480 volts « Reply #24 on: June 24, 2026, 06:18:34 PM » Author: WorldwideHIDCollectorUSA
So far, I have been using some reverse fed industrial control and general purpose step down transformers as step up transformers in addition to split phase 240V to run my lighting that requires voltages above 120V so far. I generally use a plug on the primary side and an appropriate receptacle on the secondary side of my transformers to ensure that I disconnect power easily whenever I experience problems. I just use common sense by turning off the power whenever I need to service my fixtures or step up transformers as well as never touching any exposed live components to avoid getting shocked. So far, I have used transformers to run 208-277V lighting so far, but recently acquired a transformer that I have been planning to use for 480V lighting. In particular, I have been planning to use a 460V 60Hz 1000W H36 mercury vapor reactor ballast to run one of those hard to find 880W Sylvania Unalux high pressure sodium retrofit lamps eventually. Most importantly, care must be taken when working with step up transformers for high voltage lighting applications.
« Last Edit: June 24, 2026, 06:24:07 PM by WorldwideHIDCollectorUSA » Logged

Desire to collect various light bulbs (especially HID), control gear, and fixtures from around the world.

DISCLAIMER: THE EXPERIMENTS THAT I CONDUCT INVOLVING UNUSUAL LAMP/BALLAST COMBINATIONS SHOULD NOT BE ATTEMPTED UNLESS YOU HAVE THE PROPER KNOWLEDGE. I AM NOT RESPONSIBLE FOR ANY INJURIES.

dor123
Member
*****
Offline

Gender: Male
View Posts
View Gallery

Other loves are printers/scanners/copiers, A/Cs


WWW
Re: 480 volts « Reply #25 on: June 25, 2026, 08:52:11 AM » Author: dor123
Our 3PH voltage in Israel, is 380V I think.
Logged

I"m don't speak English well, and rely on online translating to write in this site.
Please forgive me if my choice of my words looks like offensive, while that isn't my intention.

I only working with the international date format (dd.mm.yyyy).

I lives in Israel, which is a 220-240V, 50hz country.

Print 
© 2005-2026 Lighting-Gallery.net | SMF 2.0.19 | SMF © 2021, Simple Machines | Terms and Policies