Author Topic: Buzzing circuit breaker panel  (Read 6834 times)
Fluorescent05
Zack
Buzzing circuit breaker panel « on: October 15, 2020, 02:27:33 PM » Author: Fluorescent05
My electric panel seems to be buzzing. Is this the result of an overload?
Wireman
Re: Buzzing circuit breaker panel « Reply #1 on: October 15, 2020, 03:47:59 PM » Author: Wireman
Yikes! Buzzing from a circuit panel is not good. Check around the house to see if there are to many lights and appliances are running on one circuit. Chances are it's not an overload. The panel should be checked for overheating,loose breakers,loose connections, defective breakers or bus bars. The work must be done very carefully as the buzzing could be from a faulty connection.
Re: Buzzing circuit breaker panel « Reply #2 on: October 15, 2020, 04:29:28 PM » Author: Ash
Buzzing can be caused by arcing at a loose connection, which is the possibility that raises concerns
Some other causes of buzzing are contactors and transformers - if any are installed in the panel, and sometimes (more common with cheap breakers) humming of the coil of the magnetic tripping mechanism inside the breaker, even at currents below it's current rating
For a start. flip things off to find out which one is buzzing, if its' a breaker at all
Check if it's hot to touch on its front surface
Check what load is powered from it and whether it is an overload for this breaker
Open the panel user cover (that hides the connections) and inspect if there is any sign of burning on this breaker inside, at the wire terminals. Sniff it....
In US style panels with the phase busbars located at the back of the breakers, there may be also bad connection between the breaker and busbar. With the main power switched off and absence of voltage verified, remove the breaker from the busbar and inspect it's connections there (i guess it is held in place with some lug tightened with a screw or "clicks in" in some way ?)
Try to switch it on/off, see if it reacts normally and doesn't seem to stuck mechanically inside...
Xytrell
Re: Buzzing circuit breaker panel « Reply #3 on: October 15, 2020, 06:22:47 PM » Author: Xytrell
There's a chance it's relatively harmless. The fast-trip mechanism relies on a solenoid in series with the load. This may make audible noise at higher load and still be safe - similar mechanism to how older transformers are sometimes noisy. As others have pointed out, I'd still recommend looking for hot spots. Thermal cameras are great for this, but a IR thermometer would still help in a pinch.
Fluorescent05
Zack
Re: Buzzing circuit breaker panel « Reply #4 on: October 15, 2020, 07:59:47 PM » Author: Fluorescent05
I am not exactly sure, but I think the buzzing is coming from a GFCI breaker. When I trip it, it still buzzes.
Wireman
Re: Buzzing circuit breaker panel « Reply #5 on: October 15, 2020, 08:39:13 PM » Author: Wireman
Sounds like that breaker is defective and needs to be replaced.
To be sure turn off all of the other breakers except that one. If you still hear it buzzing that's most likely the problem and that it should be replaced ASAP.
What brand of panel is this? Any ideas on how old it is?
Fluorescent05
Zack
Re: Buzzing circuit breaker panel « Reply #6 on: October 15, 2020, 11:01:12 PM » Author: Fluorescent05
Actually, it might be the double pole 60 amp breaker above the GFCI. Is this even worse? I'm not sure who made the panel but all of the breakers are Square D.
Wireman
Re: Buzzing circuit breaker panel « Reply #7 on: October 15, 2020, 11:20:04 PM » Author: Wireman
it's worse in terms of safety as this breaker is for a circuit that pulls considerable current. Is this breaker for the AC/furnace? In terms of replacing it, it's no more difficult to replace than the GFCI. Does the breaker feel very warm? Again you can try what I mentioned in my previous post to see if the buzzing is coming from this breaker. Since all of the breakers are Square D that means that this is a Square D panel as they are not interchangeable with other brands. The Square D QO panels/breakers are very reliable, probably the best there is but the homeline series isn't the greatest. There may be a label or on the breakers themselves if they are QO or Homeline. If you have a picture I could easily tell by looking at the breakers and you don't have to remove the cover.
Fluorescent05
Zack
Re: Buzzing circuit breaker panel « Reply #8 on: October 15, 2020, 11:37:34 PM » Author: Fluorescent05
Here it is: https://www.lighting-gallery.net/gallery/displayimage.php?album=lastup&cat=0&pos=0&pid=187549
Re: Buzzing circuit breaker panel « Reply #9 on: October 16, 2020, 12:08:20 AM » Author: wide-lite 1000
As Ash said , it could also be a transformer inside the panel . I have seen doorbell transformers mounted inside the panel before .
Fluorescent05
Zack
Re: Buzzing circuit breaker panel « Reply #10 on: October 16, 2020, 07:30:52 AM » Author: Fluorescent05
My doorbell transformer is across the room from this panel inside the tiled ceiling. Isn't it a code violation to have things like that in a panel?
Re: Buzzing circuit breaker panel « Reply #11 on: October 16, 2020, 09:34:16 AM » Author: Medved
Why it should be?
Plus the buzz may come from other electromagnetic devices:
A contactor (controlling water heaters to operate with low tariff time,...) can buzz a lot, when the pole shielding ring breaks or when there is a dirt within the magnet...
« Last Edit: October 16, 2020, 09:37:22 AM by Medved » Logged
Wireman
Re: Buzzing circuit breaker panel « Reply #12 on: October 16, 2020, 09:52:27 AM » Author: Wireman
I know that there are variations to what is and is not allowed between here and the States, but our doorbell transformer was designed to fit in a panel or as we call it a consumer unit.
Re: Buzzing circuit breaker panel « Reply #13 on: October 16, 2020, 11:23:03 AM » Author: Mandolin Girl
The transformer is not permitted to be inside the panel, however the code does allow it to be on the exterior of the panel by attaching it to one of the knockouts.
Re: Buzzing circuit breaker panel « Reply #14 on: October 16, 2020, 11:26:46 AM » Author: Mandolin Girl
This is our consumer unit, and the transformer is on the far left.